Questions # 11:

According to ANSI/IEEE C37.20.2, wiring across a hinge shall be all of the following except:

Options:

A.

sufficiently flexible to withstand repeated door movement without sustaining damage to wire strands or insulation.

B.

installed in a flexible non-metallic conduit with a separate ground terminated at the door and at the switchgear ground bus and chosen per the minimum wire size table.

C.

a formed loop as it crosses the hinge and secured to the equipment at both ends in such a manner that negligible strain is transmitted to wire beyond the securements.

D.

No. 14 AWG and larger, and C or D stranding.

Questions # 12:

Which MCC feature is specifically listed in the guide as part of design/construction review?

Options:

A.

Main isolating switch

B.

Exciter brush rigging

C.

Conservator diaphragm

D.

Generator slip rings

Questions # 13:

According to NEMA ICS 2, a provision for pad locking shall be provided:

Options:

A.

on the door to prevent opening the combination starter door.

B.

on the external operating handle.

C.

on the wireway to prevent opening the wireway on the motor control center.

D.

on the rear door of the low voltage motor control center.

Questions # 14:

According to ANSI C57.12, the tank pressure under rated conditions of sealed transformers shall not exceed what value?

Options:

A.

One atmosphere

B.

Two atmospheres

C.

Three atmospheres

D.

Four atmospheres

Questions # 15:

According to ANSI/NETA/ATS, when performing a dielectric withstand test on each bus section, the test voltage shall be applied for how long?

Options:

A.

One second

B.

One minute

C.

One hour

D.

One day

Questions # 16:

Who should the Source Inspector notify if they believe that product quality may be compromised by schedule pressures?

Options:

A.

Master Scheduler

B.

The inspection coordinator

C.

The shop QA Manager

D.

Project Manager

Questions # 17:

What requirement shall be included in a lockout/tagout procedure?

Options:

A.

An arc flash requirement where a high level of exposure is foreseen

B.

A power testing requirement where a direct exposure situation can be detected

C.

A voltage testing requirement where there might be direct exposure to electrical hazards

D.

A voltage and current testing for direct exposure situations

Questions # 18:

The Arc Flash PPE is required for:

Options:

A.

work on control circuits with exposed electrical conductors below 120 VAC.

B.

removal of covers on properly installed wireways, junction boxes, and cable trays.

C.

voltage-testing in ac systems with work on energized conductors.

D.

insulated cable examination with no manipulation of cable.

Questions # 19:

Any reports, such as Material Test Reports, that have been modified or corrected should be:

Options:

A.

accepted after clarification.

B.

cause for immediate rejection.

C.

rejected at the discretion of the source inspector.

D.

accepted after signatures are verified.

Questions # 20:

In a Class I hazardous area, what is the maximum distance from an enclosure, containing arcing devices should a conduit seal be located?

Options:

A.

4 inches 10.16 cm away from the closest union or coupling

B.

10 inches 25.4 cm

C.

12 inches 30.48 cm

D.

18 inches 45.72 cm