Questions # 21:

The 'maximum exposed area' of the fire-rated glass is defined by the supplier as 3 sqm/32 sqft. The window area is 4 sqm/43 sqft.

What would be the best option?

Options:

A.

Do not use fire-rated glass due to the size limit and replace it with normal glass.

B.

Split the window in two equal parts using an aluminum frame.

C.

Split the window into parts smaller than specified as the maximum exposed area and ensure fire-rated frames are used.

D.

Split the window in two equal parts fitted together with transparent silicon glue.

Questions # 22:

What is the main advantage of using an End-of-Row (EoR) design?

Options:

A.

A single Top-of-Rack (ToR) switch is more expensive than an EoR switch

B.

You need a separate rack to install all your EoR switches

C.

There will be fewer switches to manage (corrected typing: original said “more”)

D.

A ToR switch has only optical interfaces

Questions # 23:

Where should perforated tiles be installed?

Options:

A.

At the back of racks

B.

Every 5th rack

C.

One tile per rack in front

D.

As close to AC as possible

Questions # 24:

In order to save energy, you are going to install an automated system to switch off lights. What should be taken into consideration when installing such a system?

Options:

A.

Security guards should perform regular inspections verifying the system works.

B.

The system should not be based on motion detection as the lights might suddenly switch off while staff is still at work.

C.

It is not advisable to use such a system since it will reduce the lifetime of LED lighting.

D.

At all times, the levels should allow for security cameras to function properly.

Questions # 25:

Management requests a 15-minute battery bank at full UPS load. UPS specs:

    30 kVA, PF 0.8

    Battery 384 V (192 cells), end discharge 308 V

    Inverter PF 0.8, 400 V output

What information is missing to perform the calculation?

Options:

A.

UPS efficiency

B.

Inverter efficiency / output PF

C.

Load imbalance

D.

Available battery charging current

Questions # 26:

You are working with a customer who requires a guarantee that THDi levels coming from the UPS should not exceed more than 3% THDi. Furthermore, he wants to run a power-efficient data center. The UPS has a 6-Pulse SCR/Thyristor based rectifier. The current load on the UPS is approximately 80%. The customer indicates they are not expecting any changes on the ICT infrastructure for the next 3 years.

What should you recommend?

Options:

A.

Nothing, the UPS will be able to take care of the right levels of THDi

B.

Install a passive harmonic filter on the UPS

C.

Install an active harmonic filter on the UPS

D.

Install an isolation transformer rated at K13 or K20

Questions # 27:

You need to determine the strategy for the cooling audit. All the servers are based on a front-to-rear (F-R) airflow design.

Which location for the temperature/humidity measurement should you recommend for the audit?

Options:

A.

At the back/rear of the server at 50 mm/2 inch

B.

At 1.5 meters/5 feet above the floor in the middle of the cold aisle

C.

At the front/intake of the server at 50 mm/2 inch

D.

At 1.5 meters/5 feet above the floor in the middle of the hot aisle

Questions # 28:

A data center is located in an area where the demand for power is higher than the utility power company is able to deliver. This results in frequent power outages and, therefore, power shedding (scheduled/controlled power shutdown for areas) is frequently applied. The mains power is more than 650 hours/year not available.

What type of generators should be installed?

Options:

A.

Standby generators should be installed in at least an N+1 configuration

B.

Continuous generators should be installed, at least in an N+1 configuration

C.

A combination of standby-, prime-, and continuous-generators, as the duration of the power outage is unpredictable. The total available capacity of the generators should be at least 500% of the data center load

D.

Continuous generators should be installed; no N+1 configuration is needed as the generators will run all the time

Questions # 29:

What is the sensible heat ratio (SHR)?

Options:

A.

Ratio of the sensible heat to the total of sensible plus latent heat to be removed from a conditioned space

B.

Ratio of the latent heat to the total of sensible plus latent heat to be removed from a conditioned space

C.

Ratio of cold-air supply to hot-air return temperature of a cooling system

D.

Ratio of the cold-aisle temperature to the hot-aisle temperature

Questions # 30:

A data center has its own power supply from the public utility and receives chilled water supply from the building owner.

What needs to be taken into consideration when calculating the PUE?

Options:

A.

Nothing, as the chiller plant in the building also uses electrical power

B.

You will need to take the value for COP of the chiller plant into consideration

C.

You will need to take a weight factor of 0.4 for district chilled water into consideration

D.

PUE calculations are not possible in shared buildings

Viewing page 3 out of 4 pages
Viewing questions 21-30 out of questions