Questions # 31:

When are the wet bulb and dry bulb temperatures identical?

Options:

A.

When the dry bulb's temperature is at the lowest allowable temperature for IT equipment as per ASHRAE

B.

When the dry bulb's temperature is at the highest allowable temperature for IT equipment as per ASHRAE

C.

When the relative humidity is at the best practice value for relative humidity, being 50% RH

D.

When the relative humidity is 100%

Questions # 32:

The humidity in the computer room has changed from about 50% down to 35% Relative Humidity (RH).

What influence does this have on Electrostatic Discharge (ESD)?

Options:

A.

No influence as long as the temperature is at approximately 20°C/77°F

B.

Relative humidity has no influence on ESD

C.

ESD levels will go up

D.

ESD levels will go down

Questions # 33:

What is the floor loading requirement for a Rated-3 data center according to ANSI/TIA-942?

Options:

A.

7.2 kPa

B.

8.4 kPa

C.

12 kPa

D.

15 kPa

Questions # 34:

Should aerosol cleaning solutions be used in the computer room?

Options:

A.

No, unless leak detection installed

B.

No, it will contaminate the room

C.

Yes, only if room smells bad

D.

Yes, if not connected to power

Questions # 35:

What is a disadvantage of hypoxic-based fire suppression?

Options:

A.

Only usable in non-occupied areas

B.

Only usable in rooms with sufficient air changes

C.

Gas containers must be close to hazard

D.

Only usable with positive pressure rooms

Questions # 36:

You want to make cooling more effective by setting cold aisle temperature to 4 °C (39 °F). Is this acceptable?

Options:

A.

Yes, but only if cooling systems can maintain this continuously

B.

Yes, as long as dewpoint doesn’t go below -9 °C (16 °F)

C.

No, 4 °C (39 °F) is below the allowable ASHRAE range

D.

No, intake air must be exactly 20 °C (68 °F)

Questions # 37:

You are allowed to use a calculator for this question. A battery bank is rated at a total capacity of 600 Ah. Calculate how much charging current the rectifier should be able to supply as charging current.

Options:

A.

12 Amperes

B.

30 Amperes

C.

60 Amperes

D.

80 Amperes

Questions # 38:

Two servers stacked with no gap (metal-to-metal). What heat transfer occurs?

Options:

A.

No heat transfer

B.

Conduction

C.

Radiation

D.

Convection

Questions # 39:

A computer room needs to be fitted out with a gas-based fire suppression system. The computer room will be a high-density data center with about 30% of the racks being closed circuit cooling blade-center racks.

Should the supplier of the fire suppression system be informed on the design of the racks?

Options:

A.

No, cooling and design of racks have no influence on the fire suppression system design.

B.

Only when the rack height obstructs a potential fire suppression release point.

C.

Yes, the design of the racks has an influence on the fire suppression system design.

D.

Only when the racks might block access to the fire panel.

Questions # 40:

The UPS of a data center, with an ANSI/TIA-942 Rating-4, is installed with the rectifier connected to power feed A and the bypass/reserve line input connected to power feed B.

To which feed will the output of the UPS be synchronized?

Options:

A.

The UPS will not synchronize to any of the feeds but use an internal clock to set the output voltage and frequency

B.

Depends on the setting of the UPS, as the UPS can normally be set to either feed

C.

Feed A

D.

Feed B

Viewing page 4 out of 4 pages